Thread Rating:
  • 315 Vote(s) - 2.69 Average
  • 1
  • 2
  • 3
  • 4
  • 5
Proteco Advantage (Q60A) Error Code "03"
#1
Hello there.
I have a problem with my Proteco automation system.

My panel of the Q60A displays: "--" (standby)

When I try to open de gate (remote control button), the panel displays: "03", and nothing happens, and the error remains there till a reset is made.

I have shorted 3-9 and 4-9 for bypassing cells.

Please let me know what this error code "03" means.

I've disconnected and reconnected most of the wires and still nothing.

Thanks in advance.
Reply
#2
Hi,
how controller reacts on open command from the terminals (1-8)?

I would disconnect everything from the panel (including motors) and leave only 19&20 connected which is 240V supply. Of course you have to leave links on safety devices and stop inputs. Then you have to give open command from the terminals 1-8 and see. If it works i would try give open command from remote. If it works i would connect one motor, then other motor then photocells and so on.
You have to check all step by step.
www.webseb.co.uk

!!! Gate and Door Automation Engineers required (London, TW) !!!
Reply
#3
Hi

In our experience with Proteco brand of automation, the above can either relate to a 'short' across the terminals or there is a failure with a component on the board. Sometimes random digits displayed have been reported to be flashing or showing in red.

In our experience, disconnecting all of the cabling but leaving links between 2-8, 3-9 and 4-9, powering down (to reset the 24v onboard fuses) and re-introducing one piece of equipment at a time until the random digits is seen will pin point the 'short'. This has been seen where intercoms have been installed as part of an installation and a feedback shock is received by the control board.

Kind Regards

Gate Motors
www.gatemotors.co.uk
Reply
#4
My Q60A shows EF - photocell test error.
When powered on it shows --. But when i try to Open/close the gate it clicks a few Times and then showa EF.

I have changed photocells it didnt help.
Then i have done per your instruction: disconnecting all of the cabling but leaving links between 2-8, 3-9 and 4-9.
And it behaves exactly the same even with everything disconnected?!?!

Is that a motherboard error?


Thanks !
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  q60a stevea 1 303 23-08-2024, 12:14 PM
Last Post: stevea
  TC fault code on Q60ar control board Skydive1710 3 4,809 20-11-2023, 03:12 PM
Last Post: NormanY
Exclamation Proteco Q60A stopped working xCO 0 1,321 19-06-2023, 01:03 PM
Last Post: xCO
  Replacement Q60A board? ndyhzlwd 1 2,642 10-02-2023, 03:19 PM
Last Post: SamA
  Q80A Fault Code kevcl15@yahoo.co.uk 1 2,718 03-02-2023, 12:00 PM
Last Post: SamA
  Proteco controller & ACT5e keypad - keeps tripping fclauson 4 4,949 26-08-2022, 03:42 PM
Last Post: JoeF
  Hello - Another Proteco Q60A/R Question! SawboMan 2 3,860 12-07-2022, 11:48 AM
Last Post: SamA
  Proteco Q60 - FH error then close after opening Needlerp 1 2,995 24-06-2022, 09:54 AM
Last Post: JamieF
  proteco q60a microcontroller program arashkhan 1 3,078 17-06-2022, 01:29 PM
Last Post: benbrooks
  Proteco Q60 AR ...Fob wont program Shane1 0 2,085 12-01-2022, 08:13 PM
Last Post: Shane1

Forum Jump:


Users browsing this thread: 1 Guest(s)