		Hi 
 
I have the BFT Regal 5 board and would like to install courtesy lights that will come on when the gate opens, and stay on..... until the gate closes. 
 
Is this facility available on the board 
 
Thanks for your help 
 
I would like to install 4x 24v led lights
	 
	
	
	
	
 
 
	
	
	
		
	Posts: 7 
	Threads: 2 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
 
	
	
	
		
	Posts: 49 
	Threads: 0 
	Joined: Sep 2013
	
 Reputation: 
 0
	 
 
	
		
		
		23-01-2015, 11:35 PM 
(This post was last modified: 23-01-2015, 11:54 PM by thm.)
		
	 
	
		You could use a magnetic contact (single-leaf gate: magnet on leaf, sensor on opposite from hinges side - double-leaf gate: magnet on one leaf, sensor on other leaf with cable running on/through leaf), a 12 VDC power supply and a 12 VDC changeover relay. 
 
Run power supply (+) through magnetic contact (gate closed: contact closed / gate open: contact open) to appropriate trigger terminal of relay and (-) directly to other trigger terminal. Run the phase, through relay (enter at COM, exit at NC), to lights and neutral directly to lights. 
 
Use a magnetic contact suitable for outside installation ("heavy-duty"), cable suitable for outside installation and, in case of double-leaf gate, for repeated bending, and that DC power supply is protected from weather but has "breathing" space to keep it cool. 
 
This setup is totally independent from the automation. 
 
You may want to use a delay-off timer after the relay (to keep lights on for some extra time after gate closes) and/or a light sensor (crepuscular sensor) so that lights stay off during the day. 
 
Remarks: 1) If power supply is off, lights will stay on. 2) You can also use this setup to create a "gate left open for too long" system by connecting a delay-on timer after the changeover relay (I prefer to use the relay output to light a warning lamp, so that I know the gate isn't closed, and the delay-on timer output to sound a buzzer, so that I know it's been in this state for too long).
	 
	
	
	
	
 
 
	
	
	
		
	Posts: 2 
	Threads: 0 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
	
	
		 (15-01-2015, 10:53 PM)MCLUMA Wrote:  Hi 
 
I have the BFT Regal 5 board and would like to install courtesy lights that will come on when the gate opens, and stay on..... until the gate closes. 
 
Is this facility available on the board 
 
Thanks for your help 
 
I would like to install 4x 24v led lights 
Terminals 12 and 13 are 240v ac outputs for courtesy lights, by default the programming is set to keep light on 90 seconds after last operation
 
Lee
	  
	
	
	
	
 
 
	
	
	
		
	Posts: 7 
	Threads: 2 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
	
		
		
		26-01-2015, 08:46 PM 
(This post was last modified: 26-01-2015, 08:54 PM by MCLUMA.)
		
	 
	
		 (25-01-2015, 09:20 PM)leeturner6 Wrote:   (15-01-2015, 10:53 PM)MCLUMA Wrote:  Hi 
 
I have the BFT Regal 5 board and would like to install courtesy lights that will come on when the gate opens, and stay on..... until the gate closes. 
 
Is this facility available on the board 
 
Thanks for your help 
 
I would like to install 4x 24v led lights  
 
 
Terminals 12 and 13 are 240v ac outputs for courtesy lights, by default the programming is set to keep light on 90 seconds after last operation 
 
Lee 
I know about these terminals but 90 sec will not work for me
  
 (23-01-2015, 11:35 PM)thm Wrote:  You could use a magnetic contact (single-leaf gate: magnet on leaf, sensor on opposite from hinges side - double-leaf gate: magnet on one leaf, sensor on other leaf with cable running on/through leaf), a 12 VDC power supply and a 12 VDC changeover relay. 
 
Run power supply (+) through magnetic contact (gate closed: contact closed / gate open: contact open) to appropriate trigger terminal of relay and (-) directly to other trigger terminal. Run the phase, through relay (enter at COM, exit at NC), to lights and neutral directly to lights. 
 
Use a magnetic contact suitable for outside installation ("heavy-duty"), cable suitable for outside installation and, in case of double-leaf gate, for repeated bending, and that DC power supply is protected from weather but has "breathing" space to keep it cool. 
 
This setup is totally independent from the automation. 
 
You may want to use a delay-off timer after the relay (to keep lights on for some extra time after gate closes) and/or a light sensor (crepuscular sensor) so that lights stay off during the day. 
 
Remarks: 1) If power supply is off, lights will stay on. 2) You can also use this setup to create a "gate left open for too long" system by connecting a delay-on timer after the changeover relay (I prefer to use the relay output to light a warning lamp, so that I know the gate isn't closed, and the delay-on timer output to sound a buzzer, so that I know it's been in this state for too long). 
Yes i have somthing like this planned, but was hoping there were terminals on the board that would have done the job for me
	  
	
	
	
	
 
 
	
	
	
		
	Posts: 49 
	Threads: 0 
	Joined: Sep 2013
	
 Reputation: 
 0
	 
 
	
		
		
		27-01-2015, 10:06 AM 
(This post was last modified: 27-01-2015, 10:09 AM by thm.)
		
	 
	
		I am not familiar with this board but can you check with a multimeter what the lock output (22 & 23) is when "suction-type" (type of lock) menu option is set to ON ?  I suspect it is 12VDC when gate is closed and 0V in any other state and so, unless you want to use an electromechanical lock, you can use it to arm a relay.
	 
	
	
	
	
 
 
	
	
	
		
	Posts: 7 
	Threads: 2 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
	
	
		 (27-01-2015, 10:06 AM)thm Wrote:  I am not familiar with this board but can you check with a multimeter what the lock output (22 & 23) is when "suction-type" (type of lock) menu option is set to ON ?  I suspect it is 12VDC when gate is closed and 0V in any other state and so, unless you want to use an electromechanical lock, you can use it to arm a relay. 
That is a very good suggestion
 
I can look into that one
	  
	
	
	
	
 
 
	
	
	
		
	Posts: 2 
	Threads: 0 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
	
		
		
		28-01-2015, 12:09 AM 
(This post was last modified: 28-01-2015, 12:14 AM by leeturner6.)
		
	 
	
		Lock outputs on gates usually only pulse for a set amount of seconds so this wouldn't work unless it also pulsed on close then you could use a latched relay, personally I would go with above mentioned independent switch
	 
	
	
	
	
 
 
	
	
	
		
	Posts: 7 
	Threads: 2 
	Joined: Jan 2015
	
 Reputation: 
 0
	 
 
	
	
		 (28-01-2015, 12:09 AM)leeturner6 Wrote:  Lock outputs on gates usually only pulse for a set amount of seconds so this wouldn't work unless it also pulsed on close then you could use a latched relay, personally I would go with above mentioned independent switch 
You are right 
had last night a quick look at the manual, and it only gives a short 12v pulse to unlock the magnetic lock, so its not going to do it for me
 
I hope to have all the items in house by this weekend so I can do the installation
 
I will do the work with a magnetic reed switch, Normally Closed, so when the gate opens the lights will switch on
 
Thanks for all the advise
	  
	
	
	
	
 
 
	
	
	
		
	Posts: 49 
	Threads: 0 
	Joined: Sep 2013
	
 Reputation: 
 0
	 
 
	
	
		 (28-01-2015, 12:09 AM)leeturner6 Wrote:  Lock outputs on gates usually only pulse for a set amount of seconds so this wouldn't work unless it also pulsed on close then you could use a latched relay, personally I would go with above mentioned independent switch 
That's the regular operation of the lock output. However, the "suction-type" => ON option looks like intended for connecting a magnetic lock, where you keep the magnet powered to keep the gate closed. At least, this is what I think the manual describes, despite the ambiguous terms used, and a multimeter could easily prove or disprove that.
	  
	
	
	
	
 
 
	 
 |