Thread Rating:
  • 406 Vote(s) - 2.75 Average
  • 1
  • 2
  • 3
  • 4
  • 5
PROTECO Q60S/R FAULT AND INSTALL
#3
(30-04-2012, 08:43 AM)Proteco_UK Wrote: Hi

The Q60SR control board for swing gates showing "GO" error means that the control board is receiving a constant start signal caused by a closed circuit across terminals 1 & 8 (manual start command). This can be caused by incorrect wiring of push button switches, intercom connections and loop detectors. Anything that starts the gate other than the remote control key fobs will generate a "manual start command".

I would first remove all wiring from just terminal 1. This will remove the "GO" error and the gate may start. If it does, wait for the operation to complete, then you will see "- -" on the screen (stand by mode). Once this is seen, re-introduce one connection at a time back to terminal 1 until you see "GO" appear and stays there. As long as you know which piece of equipment is identified to terminal 1, you will be able to pin-point the unit causing the short.

If you require further info, please contact us as Gate Motors - support@gatemotors.co.uk

Kind Regards

Gate Motors technical Support
01202 717191

hi thanks it was a problem on that but manafactuers fault did not clear when i undone links so gone back for replacement.
thanks jeff
Reply


Messages In This Thread
RE: PROTECO Q60S/R FAULT AND INSTALL - by jeffducati - 30-04-2012, 04:20 PM
RE: PROTECO Q60S/R FAULT AND INSTALL - by cciprian - 14-06-2012, 09:07 PM

Possibly Related Threads…
Thread Author Replies Views Last Post
  PROTECO Q60S BOARD DHOB123 0 7,057 02-08-2017, 10:52 PM
Last Post: DHOB123
  D5131GB FAULT Carlo 10 38,874 08-01-2017, 05:23 PM
Last Post: Access-Control-Ltd
  Q60S/R - Error code "P" DanyJee 0 7,344 04-06-2016, 10:42 AM
Last Post: DanyJee

Forum Jump:


Users browsing this thread: 1 Guest(s)