Hello, trying to connect Came DOC E photocells to Came za3 panel but no success with it, would be grateful if someone would have a detailed plan of it ,position of dip switches etc. Thanks---Billy
first of all how many pairs of photocell are you connecting?
I'll presume the bare minimum of 1 set.
photocell >>>>> ZA3 panel
+ >>>>>>>>>>>>>>>10
->>>>>>>>>>>>>>>11
com>>>>>>>>>>>>>>> 2
n/c >>>>>>>>>>>>>>> c1
dip switches on doc e cells
1 - off(down) 1 pair of photocells
2 - off(down) 24v system
dip switches on za3 panel
1-on
2-off
3-off
4-off
5-off
6-off
7-off
8-on
9-off
make sure you have a link between 1 and 2 in the za3 this is the stop circuit.
trimmers in za3
tl roughly about 6 o'clock needs to make the motors run for an extra 8 or so seconds after fully opening or closing.
tca somewhere near 5 o'clock will give you about 35 seconds opening waiting period.
rt2m this is the second leaf delay so if you have a catchment strip you need to adjust this accordingly.there is a minimum 2nd leaf delay of 1 second in this panel.
If the wrong motor moves first swap the 2 bunches of motor leads over
u,v,w into x,w,y
if one of the motors moves in a different direction to the other swap either u ,v or x,y over depending on which motor it is.
regards Johnathan Barker
just to add to the very helpful post by johnathan here is the instruction manual for the CAME ZA3 Control board for your reference.