Gate Controls/Indicators 200m from Gates
#1
I'm trying to place an additional set of gate controls in my house for existing gates which are roughly 200m away. My gate controller is a CTR32. The manual is here:
https://www.knowledgebase.egates.co.uk/f...p?id=10686

All the features I want to install seem to be available on the controller I have.
1) An open/start button (normally open)
2) Gate open light (240v)
3) Blinker light to indicate opening/closing sequence (240v)

If the controls were being installed 5m from the gate I would be happy getting on with it as I'm competent enough to do the wiring.
What I'm not sure about is running cables 200m. I already have ducting all the way from the gates to the house, so the route is not a problem, however I'm unsure as to whether I need to make any special allowances for the length of cable run. I only want a very low-current light for the gate open and blinker indicators, so what sort of cable should I use for those and the open switch itself?

Any help you can offer would be greatly appreciated.
#2
Morning!

For any gate open switch over this distance, i would recommend a GSM controller. This would wire into the normally open switch of the gate control board and accept a call from a telephone number which will then open the gates. The gate control board will then send voltage to the gate open light/flashing light. You can find GSM controllers in the link below.
http://www.easygates.co.uk/gsm-controller.asp

I hope this helps.
EasyGates.co.uk
 
EG Direct - Trade only

Smart and Secure - Smart Home Shop

Smart Home Matters - Smart Home News
#3
Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house. Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not. Therefore we need to have some indicator in the house of the gate's open/closed status as well as the ability to open or close it, otherwise we've no idea whether we are opening a closed gate, or closing an open one!
#4
(31-05-2017, 11:37 AM)ADickson Wrote: Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house. Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not. Therefore we need to have some indicator in the house of the gate's open/closed status as well as the ability to open or close it, otherwise we've no idea whether we are opening a closed gate, or closing an open one!

hi
all you need is professional radio-receiver with lcd - screen to control relay status . that have to be superheterodyna receiver module , range 200-1000 m
Best Regards 
Tom 
Automatic-TC
#5
(31-05-2017, 11:37 AM)ADicksoen Wrote: Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house from  Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not.

That is quite a distance.
#6
(19-06-2017, 03:47 PM)Hardee Wrote:
(31-05-2017, 11:37 AM)ADicksoen Wrote: Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house from Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not.

That is quite a distance.

With this much distance, it's really difficult to get good signal strength.
#7
(17-10-2018, 07:33 PM)alleno Wrote:
(19-06-2017, 03:47 PM)Hardee Wrote:
(31-05-2017, 11:37 AM)ADicksoen Wrote: Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house from Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not.

That is quite a distance.

With this much distance, it's really difficult to get good signal strength.

I agree with you mate, it will be difficult to get a strong signal with that distance
#8
(07-05-2019, 10:46 PM)iamashleywilcox Wrote:
(17-10-2018, 07:33 PM)alleno Wrote:
(19-06-2017, 03:47 PM)Hardee Wrote:
(31-05-2017, 11:37 AM)ADicksoen Wrote: Thanks Ryan.

We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house from Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not.

That is quite a distance.

With this much distance, it's really difficult to get good signal strength.

I agree with you mate, it will be difficult to get a strong signal with that distance
Hi, have you possibly tried using a designated Ariel to boost signal strength.
EasyGates.co.uk - EasyGates Ltd
 
EasyGates Direct - Trade only accounts.

Smart and Secure Center - Smart Home Products
#9
(31-05-2017, 11:37 AM)ADicksons Wrote: We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house. Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not. Therefore we need  to have some indicator in the house of the gate's open/closed status as well as the ability to open or close it, otherwise we've no idea whether we are opening a closed gate, or closing an open one!

There is an indicator placed directly below the inspection door on the front of the Kleener.
#10
(14-05-2019, 11:05 PM)ArthurBrown Wrote:
(31-05-2017, 11:37 AM)ADicksons Wrote: We do already have a GSM unit on the gate, but due to the very poor signal in this area, it is unreliable.

The other problem we have is that the gate is out of sight from the house. Although it's only 200m in a straight line, it is roughly a 500m walk to get from the house to a point where you can see whether the gate is open or not. Therefore we need to have some indicator in the house of the gate's open/closed status as well as the ability to open or close it, otherwise we've no idea whether we are opening a closed gate, or closing an open one!

There is an indicator placed directly below the inspection door on the front of the Kleener.

With GSM systems it is unfortunately hit and miss you could possibly try a different network we find Vodafone usually being the best network.
EasyGates.co.uk - EasyGates Ltd
 
EasyGates Direct - Trade only accounts.

Smart and Secure Center - Smart Home Products


Possibly Related Threads…
Thread Author Replies Views Last Post
  Came ZA3 gates stuck open Ivorwindybottom 0 258 18-02-2024, 06:29 PM
Last Post: Ivorwindybottom
  Electric Gates with AllMatic BIOS2 Unit antsnaith 3 1,198 31-01-2024, 08:22 AM
Last Post: patronsecurity
  Came gates za3p Webby 4 8,819 07-01-2024, 07:11 PM
Last Post: Simon NW
  Nice Gates not closing StuL 1 1,349 24-08-2023, 01:34 PM
Last Post: JoeF
  Gates Opening After Closing tht7 2 9,458 30-07-2023, 12:30 PM
Last Post: lcpbarbosa
  Holding the Gate Open mgb 1 3,465 11-07-2023, 01:35 PM
Last Post: JoeF
  FAAC 740 Sliding gate Just closes or Stops Paul L 1 3,756 03-07-2023, 08:54 AM
Last Post: Michael
  BFT gate and Hikvision wiring help Gowrie 0 3,375 26-05-2023, 02:05 AM
Last Post: Gowrie
  Control Unit CLB202 Gate leaf learning issue Kaala1 0 3,297 25-05-2023, 03:55 PM
Last Post: Kaala1
  Hikvision DS-KD8003-IME1 video intercom to Nice Robus 600 gate motor help j1000 20 16,193 15-05-2023, 11:25 AM
Last Post: Nemen3242

Forum Jump:


Users browsing this thread: 2 Guest(s)