Commissioning, Liftmaster Sub300, CB11,Daitem D5731gb
23-04-2012, 12:31 AM
Post: #1
Commissioning, Liftmaster Sub300, CB11,Daitem D5731gb
Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?

Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.

Is there any other commissioning points need to be carried out?

All comments and advice appreciated.

Regards
sundial
Find all posts by this user
Quote this message in a reply
23-04-2012, 10:07 AM
Post: #2
RE: Commissioning, Liftmaster Sub300, CB11,Daitem D5731gb
[/color]Thank you for your enquiry the replys to you questions are below in Red



(23-04-2012 12:31 AM)sundial Wrote:  Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

The Motors are over running they should over run by about 3 seconds this is what gives the holding force in open or closed possition. If they are over running by 15 seconds then you need to reprogramme the limits so they only over run by max 3 seconds otherwise this will lead to the motors heating up and wearing out quicker.


The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?



If you have 1 x set of photocells i would wire them into just the close circuit ie pins 22 and 24 then the gates will revesre upon closing. You dont need to link out the unused circuits.



Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.



The only way to achieve this is with a switch wired into the system accross pins 17 & 20 this will hold the gates open untill the switch is releases. By Isolating the power in the open possition the motors will get confused and over run when you switch power back on and cause wear or damage to the motors.


Is there any other commissioning points need to be carried out?


[color=#FF0000]

You need to check that the system is safe and complys with the EN Safety regulations please read through the attatched regulation guide which in EN Law regarding Electric Gates.

Any more questions please contact our technical
advisors who will be able to help

All comments and advice appreciated.

Regards
sundial


Attached File(s)
.pdf  GATE SAFETY LEGISLATION GUIDE.pdf (Size: 1.37 MB / Downloads: 54)

[Image: header-2008_r1_c1.gif]

Easygates Technical Support Team

www.easygates.co.uk

Tel: 0845 054 5070
Find all posts by this user
Quote this message in a reply
24-04-2012, 09:07 AM (This post was last modified: 24-04-2012 09:11 AM by sundial.)
Post: #3
RE: Commissioning, Liftmaster Sub300, CB11,Daitem D5731gb
Hello Mark, Thanks for your answers to my questions, I have implemented your answers for question 1 and 2.see below

Would like to know how do I implement your answer 3, and what way will it be operated, would only want to have the gates to remain in the open position at certain times, do I use a relay (12 or 24v)

All help and assistance appreciated

Regards
sundial

Sean
johnf4@mac.com

=============================================
On 23 Apr 2012, at 10:07, Electric Gate Automation Forums wrote:

sundial Wrote: Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

Question 1. After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

Answer 1. The Motors are over running they should over run by about 3 seconds this is what gives the holding force in open or closed possition. If they are over running by 15 seconds then you need to reprogramme the limits so they only over run by max 3 seconds otherwise this will lead to the motors heating up and wearing out quicker.


Question 2. The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?

Answer 2. If you have 1 x set of photocells i would wire them into just the close circuit ie pins 22 and 24 then the gates will revesre upon closing. You dont need to link out the unused circuits.



Question 3. Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.



Answer 3. The only way to achieve this is with a switch wired into the system accross pins 17 & 20 this will hold the gates open untill the switch is releases. By Isolating the power in the open possition the motors will get confused and over run when you switch power back on and cause wear or damage to the motors.


Is there any other commissioning points need to be carried out?




You need to check that the system is safe and complys with the EN Safety regulations please read through the attatched regulation guide which in EN Law regarding Electric Gates.

Any more questions please contact our technical advisors who will be able to help

All comments and advice appreciated.

Regards
sundial

(23-04-2012 10:07 AM)Mark Wrote:  Thank you for your enquiry the replys to you questions are below in Red



(23-04-2012 12:31 AM)sundial Wrote:  Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

The Motors are over running they should over run by about 3 seconds this is what gives the holding force in open or closed possition. If they are over running by 15 seconds then you need to reprogramme the limits so they only over run by max 3 seconds otherwise this will lead to the motors heating up and wearing out quicker.


The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?



If you have 1 x set of photocells i would wire them into just the close circuit ie pins 22 and 24 then the gates will revesre upon closing. You dont need to link out the unused circuits.



Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.



The only way to achieve this is with a switch wired into the system accross pins 17 & 20 this will hold the gates open untill the switch is releases. By Isolating the power in the open possition the motors will get confused and over run when you switch power back on and cause wear or damage to the motors.


Is there any other commissioning points need to be carried out?


[color=#FF0000]

You need to check that the system is safe and complys with the EN Safety regulations please read through the attatched regulation guide which in EN Law regarding Electric Gates.

Any more questions please contact our technical
advisors who will be able to help

All comments and advice appreciated.

Regards
sundial
Find all posts by this user
Quote this message in a reply
24-04-2012, 12:55 PM
Post: #4
RE: Commissioning, Liftmaster Sub300, CB11,Daitem D5731gb
(24-04-2012 09:07 AM)sundial Wrote:  Hello Mark, Thanks for your answers to my questions, I have implemented your answers for question 1 and 2.see below

Would like to know how do I implement your answer 3, and what way will it be operated, would only want to have the gates to remain in the open position at certain times, do I use a relay (12 or 24v)

All help and assistance appreciated

Regards
sundial

Sean
johnf4@mac.com

=============================================
On 23 Apr 2012, at 10:07, Electric Gate Automation Forums wrote:

sundial Wrote: Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

Question 1. After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

Answer 1. The Motors are over running they should over run by about 3 seconds this is what gives the holding force in open or closed possition. If they are over running by 15 seconds then you need to reprogramme the limits so they only over run by max 3 seconds otherwise this will lead to the motors heating up and wearing out quicker.


Question 2. The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?

Answer 2. If you have 1 x set of photocells i would wire them into just the close circuit ie pins 22 and 24 then the gates will revesre upon closing. You dont need to link out the unused circuits.



Question 3. Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.



Answer 3. The only way to achieve this is with a switch wired into the system accross pins 17 & 20 this will hold the gates open untill the switch is releases. By Isolating the power in the open possition the motors will get confused and over run when you switch power back on and cause wear or damage to the motors.


Is there any other commissioning points need to be carried out?




You need to check that the system is safe and complys with the EN Safety regulations please read through the attatched regulation guide which in EN Law regarding Electric Gates.

Any more questions please contact our technical advisors who will be able to help

All comments and advice appreciated.

Regards
sundial

(23-04-2012 10:07 AM)Mark Wrote:  Thank you for your enquiry the replys to you questions are below in Red



(23-04-2012 12:31 AM)sundial Wrote:  Hello

Have just got my gates operating.

System I have is a 2 wing gate, Liftmaster sub300M, CB11 controller, combined with a Daitem D5731GB Wireless system. System is operating with Remotes and wireless system.

I have few questions:

After the gates are fully open or closed, the motors continue to hum for about 15 seconds. Is this a problem? if so what have I to do to rectify problem.

The Motors are over running they should over run by about 3 seconds this is what gives the holding force in open or closed possition. If they are over running by 15 seconds then you need to reprogramme the limits so they only over run by max 3 seconds otherwise this will lead to the motors heating up and wearing out quicker.


The gates closes or opens even when I block the photocell beams, I am assuming this is not correct. The photocells I have fitted are the 771E/770E and are wired as per page GB-6 that is to terminal 23 and 24. Do I need to link out 21,22, and 23?



If you have 1 x set of photocells i would wire them into just the close circuit ie pins 22 and 24 then the gates will revesre upon closing. You dont need to link out the unused circuits.



Some times I need to leave the gates in an open position, can this be done automatically, if so how? I now turn off isolator!!!.



The only way to achieve this is with a switch wired into the system accross pins 17 & 20 this will hold the gates open untill the switch is releases. By Isolating the power in the open possition the motors will get confused and over run when you switch power back on and cause wear or damage to the motors.


Is there any other commissioning points need to be carried out?


[color=#FF0000]

You need to check that the system is safe and complys with the EN Safety regulations please read through the attatched regulation guide which in EN Law regarding Electric Gates.

Any more questions please contact our technical
advisors who will be able to help

All comments and advice appreciated.

Regards
sundial

The only way to do this is either with a latching relay on the output of the lock release for the D5731GB (pins 1 & 2) I have not done this before as we don’t have any latching relay items in stock but electrically it should work.

Also to do this from remote control you would need a latching radio reciever same principle applies

[Image: header-2008_r1_c1.gif]

Easygates Technical Support Team

www.easygates.co.uk

Tel: 0845 054 5070
Find all posts by this user
Quote this message in a reply
Post Reply 


Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  LiftMaster Garage Door Problem Diagnosis easygates 0 608 05-10-2012 12:15 PM
Last Post: easygates
  >>> CB11 F.A.Q and Quick Setup Guide <<< easygates 1 2,880 20-04-2010 03:03 PM
Last Post: easygates
  >> Liftmaster CB11 Support Diagrams << easygates 1 4,064 27-04-2009 12:49 PM
Last Post: easygates
  >> Liftmaster CB24 Support Diagrams << easygates 3 4,154 27-04-2009 10:58 AM
Last Post: easygates
  >>> Liftmaster CB24 Simple Setup Guide <<< easygates 0 2,578 30-03-2009 04:27 PM
Last Post: easygates

Forum Jump:


Nice for You Electric Gates from EasyGates.co.uk